Yeah but 6.2.4.3 for the closed head system sends you to 6.2.2.3.  Granted
this is under the heading for deluge foam but the relevant section sends you
there so it's enforceable. And anything specific in 409 that conflicts with
13 overrides 13.  So as I see it you will have 3 lines in a 25' bay.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Thursday, February 25, 2010 1:41 PM
To: [email protected]
Subject: RE: Aircraft Hangar Question of the Day!

6.2.4 Closed-Head Water Sprinkler Systems for Aircraft Storage
and Servicing Areas.
6.2.4.1" Sprinkler systems shall be either wet pipe or preaction,
designed and installed in accordance with the applicable
sections of NFPA 13 and the provisions of this chapter.

If 13 allows it for wet systems, so does 409 as stated above, so since 13
allows the 12'6" in 25' bays so does 409.

I believe your reading the 12' max spacing from the foam or deluge sections,
not the closed head water sprinkler system section.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ray Vance
Sent: Thursday, February 25, 2010 12:22 PM
To: [email protected]
Subject: Aircraft Hangar Question of the Day!

To my esteemed colleagues:

I have an aircraft hangar I am looking at and would like clarification on
sprinkler / branchline spacing. I know what I think ;-)
However, I would like the combined knowledge of all of you as to the actual
requirements of the NFPA standards.

The hangar is a 32,000 suare feet Group-I hanger with a door opening to
accomodate a 36 ft tail height.
The chosen fire protection scheme is Option-3, a closed-head wet-pipe
sprinkler system at .17 gpm / 15,000 square feet and a low-level hi-ex foam
system.
The building is a metal-purlin building with 25 ft bay spacing.

NFPA-409 requires a maximum 130 sf sprinkler spacing with a maximum distance
of 12 feet between the sprinklers or the branch-lines.
NFPA-409 does not reference NFPA-13 for sprinkler or branch-line spacing.

Question:

In a building with 25 ft bays would one be allowed to space the branch-lines
at 12'-6" as indicated in NFPA-13 for storage bays at 25 feet spacing in
lieu of the 12 feet as indicated in NFPA-409?

Thanks,

Ray Vance - SET
Chief Sales Designer
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com<http://www.waynefire.com>
407-877-5563   office
321-436-2184   mobile

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to