I am working on a restaurant. The roof structure is wood trusses and the entire building has a ceiling in it varying from 9-0 to 11-6, bottom of truss is at 12-0. The roof trusses/roof deck are on a continuous slope (¼:12) from 16-1 at the highest point to 14-6 at the lowest point. Can I utilize 11.2.3.2.3 in the area between the ceiling and the roof deck? And if so do I use the 16-1 elevation or the highest height dimension between the ceiling and the roof deck? I am using quick response standard spray brass upright sprinklers.
Thank You, Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)