There is ACT in all areas except one portion of the seating area has a
suspended plywood ceiling separated from the ACT by soffits. The roof deck
has insulation/single layer membrane, so no dry system. One wet system
throughout. I couldn’t find a reason not to apply this and my thoughts were
the uprights above the ceiling are protecting that area from the ceiling to
the deck, but just wanted to be safe.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
[email protected]
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Friday, March 12, 2010 1:30 PM
To: [email protected]
Subject: RE: Reduction of remote area

I'm assuming a continuous clg. with what I'm about to say.  You can use RRA
on both levels.  Another assumption is you don't have a dry system in the
trusses.  Below the clg. you use 11'6" for the RRA calc and above the clg.
you use the greatest distance between clg and deck.  But it looks like you'd
never be over 10' so it's moot you get the full 30% reduction. 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Friday, March 12, 2010 12:34 PM
To: [email protected]
Subject: Reduction of remote area

I am working on a restaurant. The roof structure is wood trusses and the
entire building has a ceiling in it varying from 9’-0 to 11’-6, bottom of
truss is at 12’-0. The roof trusses/roof deck are on a continuous slope
(¼:12) from 16’-1 at the highest point to 14’-6 at the lowest point. Can I
utilize 11.2.3.2.3 in the area between the ceiling and the roof deck? And if
so do I use the 16’-1 elevation or the highest height dimension between the
ceiling and the roof deck? I am using quick response standard spray brass
upright sprinklers.

 

Thank You,

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - www.avg.com 
Version: 9.0.733 / Virus Database: 271.1.1/2739 - Release Date: 03/12/10
03:42:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to