I'm assuming a continuous clg. with what I'm about to say. You can use RRA on both levels. Another assumption is you don't have a dry system in the trusses. Below the clg. you use 11'6" for the RRA calc and above the clg. you use the greatest distance between clg and deck. But it looks like you'd never be over 10' so it's moot you get the full 30% reduction.
Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Friday, March 12, 2010 12:34 PM To: [email protected] Subject: Reduction of remote area I am working on a restaurant. The roof structure is wood trusses and the entire building has a ceiling in it varying from 9-0 to 11-6, bottom of truss is at 12-0. The roof trusses/roof deck are on a continuous slope (¼:12) from 16-1 at the highest point to 14-6 at the lowest point. Can I utilize 11.2.3.2.3 in the area between the ceiling and the roof deck? And if so do I use the 16-1 elevation or the highest height dimension between the ceiling and the roof deck? I am using quick response standard spray brass upright sprinklers. Thank You, Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)