I have spent a considerable amount of time and effort on this exact issue and I 
have learned some cool things.

The pressure loss data provided by some of the manufacturers is and incomplete 
chart. i.e. a 5/8" meter cuts off at 20 gpm at a pressure loss of 8 psi. When 
pressed, the manufacturer sent me a complete chart that shows a curve in which 
the meter will actually flow all the way up to 50 gpm with huge pressure 
losses. More importantly however, is that the meter will flow 26 gpm at a loss 
of approximately 14 psi. Therefore you can get an existing meter to work 
sometimes for "easy" existing homes. You have to dig and push for this info 
though.

We also learned that in the last several years, some Water Purveyors have 
started running their tap to meter line out of 1" tubing regardless of meter 
size in the event the owner wants to change them to 1" meters in the future. 
This was primarily started due to owners adding lawn irrigation I understand. 
That fact can sometimes make a tremendous difference if you have the service 
coming from the other side of the street so it is worth checking out.

Also, we have had multiple homes in which there were service tie ins and meters 
of 3/4" pipe and 3/4" meters where the system will work if the fire main is 
immediately upsized after the meter to larger pipe. The meter will flow the 
water, and the 3/4" pipe will carry the water, just not over a great distance 
without losing too much pressure.


We partnered with the Local City and County and just recently persuaded the 
largest water purveyor to waive the impact fees for the 1" meters when the sole 
purpose for the upsize is for fire protection use.

Hope this helps.

Greg McGahan

Living Water Fire Protection
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Kowkabany
Sent: Tuesday, March 16, 2010 7:54 AM
To: [email protected]
Subject: Size of Residentail Water Taps, Fees, Meters, and Backflow Preventers

The fire department and local water utility of Jacksonville are currently
working together to figure out what will be required for the new residential
sprinkler requirement.  I've been invited to participate and they are
looking to me to provide some guidance on what will be required for each new
single family home in terms of water hookups to accommodate a new 13D
system.

 

Somehow, the water department got the idea that they will need 2" taps for
each house.  I know that is way too big, but I am curious - what have you
been seeing for line sizes for single family homes?  Also, has it typically
been a single line or two separate taps.  I would think that a 1" service
would suffice for a two head calc and max flow of 30 gpm or so with average
water supplies.  It's pretty flat here and this utility is fairly consistent
with water supplies that test at 60/50 at 1,000 gpm or so.  I'm also curious
about any special meter requirements, backflow requirements, or tap fees
that your area is implementing.

 

Any feedback would be great appreciated and helpful for us in setting the
course for what will hopefully be the beginning a new era in Florida where
each new house is sprinklered.

 

Thanks for your help,

 

 

Steve Kowkabany, P.E.

Fire Protection Engineer

Neptune Fire Protection Engineering LLC

60 Ocean Boulevard, Suite 15

Atlantic Beach, FL 32233

904-652-4200 Phone

904-212-0868 Fax 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to