Will you be adding concurrent domestic flow allowance?   If so, will the AHJ's 
require it to be counted against the meter size?

There are  3/4" meters rated for 35GPM that will adequately serve many 
2-sprinkler demands;  I would recommend 1" min service lateral size and 3/4" 
min meters and try to negotiate an up-size option that won't cost thousands of 
$$   that way the homebuilder and sprinkler designer can fine-tune the design 
and the water service.



Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "G. Tim Stone" <[email protected]>
Date: Tue, 16 Mar 2010 06:14:56 
To: <[email protected]>
Subject: RE: Size of Residential Water Taps, Fees, Meters,and Backflow 
Preventers

Steve, 
Construction details for the house may determine water line size also. 
Homes with steeply pitched ceilings may require the designer to include 
extra heads in the design area. Residential heads are not listed for 
ceilings with pitches greater than 8 in 12. I believe a 2" water line into 
the structure would be the safer bet no matter what the design of the house 
is. 
G. Tim Stone 
 
NICET Level III Engineering Technician 
Fire Protection Sprinkler Design 
and Consulting Services 
117 Old Stage Rd. - Essex Jct., VT. 05452 
TEL: (802) 434-2968          Fax: (802) 434-4343 
                [email protected] 
> -----Original Message----- 
> From: [email protected] [mailto:sprinklerforum- 
> <mailto:sprinklerforum-> 
> [email protected]] On Behalf Of Steve Kowkabany 
> Sent: Tuesday, March 16, 2010 8:54 AM 
> To: [email protected] 
> Subject: Size of Residentail Water Taps, Fees, Meters, and Backflow 
> Preventers 
> 
> The fire department and local water utility of Jacksonville are 
> currently 
> working together to figure out what will be required for the new 
> residential 
> sprinkler requirement.  I've been invited to participate and they are 
> looking to me to provide some guidance on what will be required for 
> each new 
> single family home in terms of water hookups to accommodate a new 13D 
> system. 
> 
> 
> 
> Somehow, the water department got the idea that they will need 2" taps 
> for 
> each house.  I know that is way too big, but I am curious - what have 
> you 
> been seeing for line sizes for single family homes?  Also, has it 
> typically 
> been a single line or two separate taps.  I would think that a 1" 
> service 
> would suffice for a two head calc and max flow of 30 gpm or so with 
> average 
> water supplies.  It's pretty flat here and this utility is fairly 
> consistent 
> with water supplies that test at 60/50 at 1,000 gpm or so.  I'm also 
> curious 
> about any special meter requirements, backflow requirements, or tap 
> fees 
> that your area is implementing. 
> 
> 
> 
> Any feedback would be great appreciated and helpful for us in setting 
> the 
> course for what will hopefully be the beginning a new era in Florida 
> where 
> each new house is sprinklered. 
> 
> 
> 
> Thanks for your help, 
> 
> 
> 
> 
> 
> Steve Kowkabany, P.E. 
> 
> Fire Protection Engineer 
> 
> Neptune Fire Protection Engineering LLC 
> 
> 60 Ocean Boulevard, Suite 15 
> 
> Atlantic Beach, FL 32233 
> 
> 904-652-4200 Phone 
> 
> 904-212-0868 Fax 
> 
> 
> 
> _______________________________________________ 
> Sprinklerforum mailing list 
> [email protected] 
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
> <http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> 
> 
> For Technical Assistance, send an email to: [email protected] 
> 
> To Unsubscribe, send an email to:Sprinklerforum- 
> [email protected] 
> (Put the word unsubscribe in the subject field) 
_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> 
For Technical Assistance, send an email to: [email protected] 
To Unsubscribe, send an email to:[email protected] 
(Put the word unsubscribe in the subject field) 
  
__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 4946 (20100315)__________ 
The message was checked by ESET NOD32 Antivirus. 
http://www.eset.com <http://www.eset.com> 
  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to