Yes, that is dumb.  Not only does 13 not require electrical air supervision, 25 
only requires that the gauge on the air side be checked once a week.  Yet in 
the '08 edition of 25, we now require an air pressure test at 40 psi for two 
hours.  If it drops more than 3 psi in that time, then air leaks must be 
addressed.  Sounds like we need to require either electrical air supervision on 
all dry systems or recorded inspections of gauges not less than daily.
 
This entire subject area needs to be coordinated in 13 and 25.  No Roland, I am 
not volunteering to prepare the proposals, but will put it on my "when all 
caught up on everything else list, do it" to do list.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 


--- On Fri, 3/19/10, Roland Huggins <[email protected]> wrote:


From: Roland Huggins <[email protected]>
Subject: Re: Hard wired air compressors
To: [email protected]
Date: Friday, March 19, 2010, 9:54 AM


This question and especially the leap to impairment if not hard-wired  
started off with a false premise.  Who says the air supply has to be  
automatic?  It is certainly a best practice which we virtually always  
do, but if the owner is happy with using a manual air supply, that  
complies.  Now isn't that dumb!

Roland

On Mar 18, 2010, at 11:16 AM, Greg McGahan wrote:

> This is a friendly discussion and not a conflict. However, please see
> the interpretation below.
>
>
>
> 13-7.2.6.2.1 states, the air supply shall be from a source available  
> at
> all times.  A plug-in air compressor is portable and would not meet  
> the
> 'all times' criteria.  Hence, my interpretation that the compressor
> would have to be hard wired.
>
>
>
> Has this been discussed previously?
>
>
>
> Thanks
>
>
>
>
>
> Greg McGahan
>
> Operations Manager
>
>
>
> Living Water Fire Protection
>
> 1160 McKenzie Road
>
> P.O. Box 877
>
> Cantonment, Florida 32533
>
> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>
> [email protected] <mailto:[email protected]>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to