Yes, that is dumb. Not only does 13 not require electrical air supervision, 25 only requires that the gauge on the air side be checked once a week. Yet in the '08 edition of 25, we now require an air pressure test at 40 psi for two hours. If it drops more than 3 psi in that time, then air leaks must be addressed. Sounds like we need to require either electrical air supervision on all dry systems or recorded inspections of gauges not less than daily. This entire subject area needs to be coordinated in 13 and 25. No Roland, I am not volunteering to prepare the proposals, but will put it on my "when all caught up on everything else list, do it" to do list.
Dave David A. de Vries, P.E., CSP Firetech Engineering Incorporated --- On Fri, 3/19/10, Roland Huggins <[email protected]> wrote: From: Roland Huggins <[email protected]> Subject: Re: Hard wired air compressors To: [email protected] Date: Friday, March 19, 2010, 9:54 AM This question and especially the leap to impairment if not hard-wired started off with a false premise. Who says the air supply has to be automatic? It is certainly a best practice which we virtually always do, but if the owner is happy with using a manual air supply, that complies. Now isn't that dumb! Roland On Mar 18, 2010, at 11:16 AM, Greg McGahan wrote: > This is a friendly discussion and not a conflict. However, please see > the interpretation below. > > > > 13-7.2.6.2.1 states, the air supply shall be from a source available > at > all times. A plug-in air compressor is portable and would not meet > the > 'all times' criteria. Hence, my interpretation that the compressor > would have to be hard wired. > > > > Has this been discussed previously? > > > > Thanks > > > > > > Greg McGahan > > Operations Manager > > > > Living Water Fire Protection > > 1160 McKenzie Road > > P.O. Box 877 > > Cantonment, Florida 32533 > > (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231 > > [email protected] <mailto:[email protected]> > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)