David,

Could you put my pending proposals onto your list also. It would
really help me out. Mille ringraziamenti

On Fri, Mar 19, 2010 at 8:46 AM, David de Vries
<[email protected]> wrote:
> Yes, that is dumb.  Not only does 13 not require electrical air supervision, 
> 25 only requires that the gauge on the air side be checked once a week.  Yet 
> in the '08 edition of 25, we now require an air pressure test at 40 psi for 
> two hours.  If it drops more than 3 psi in that time, then air leaks must be 
> addressed.  Sounds like we need to require either electrical air supervision 
> on all dry systems or recorded inspections of gauges not less than daily.
>
> This entire subject area needs to be coordinated in 13 and 25.  No Roland, I 
> am not volunteering to prepare the proposals, but will put it on my "when all 
> caught up on everything else list, do it" to do list.
>
> Dave
>
> David A. de Vries, P.E., CSP
> Firetech Engineering Incorporated
>
>
> --- On Fri, 3/19/10, Roland Huggins <[email protected]> wrote:
>
>
> From: Roland Huggins <[email protected]>
> Subject: Re: Hard wired air compressors
> To: [email protected]
> Date: Friday, March 19, 2010, 9:54 AM
>
>
> This question and especially the leap to impairment if not hard-wired
> started off with a false premise.  Who says the air supply has to be
> automatic?  It is certainly a best practice which we virtually always
> do, but if the owner is happy with using a manual air supply, that
> complies.  Now isn't that dumb!
>
> Roland
>
> On Mar 18, 2010, at 11:16 AM, Greg McGahan wrote:
>
>> This is a friendly discussion and not a conflict. However, please see
>> the interpretation below.
>>
>>
>>
>> 13-7.2.6.2.1 states, the air supply shall be from a source available
>> at
>> all times.  A plug-in air compressor is portable and would not meet
>> the
>> 'all times' criteria.  Hence, my interpretation that the compressor
>> would have to be hard wired.
>>
>>
>>
>> Has this been discussed previously?
>>
>>
>>
>> Thanks
>>
>>
>>
>>
>>
>> Greg McGahan
>>
>> Operations Manager
>>
>>
>>
>> Living Water Fire Protection
>>
>> 1160 McKenzie Road
>>
>> P.O. Box 877
>>
>> Cantonment, Florida 32533
>>
>> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
>>
>> [email protected] <mailto:[email protected]>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to