And where you'd be putting the ball drip, a leak at the mech tee doesn't
matter much- you're installing a leak.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Friday, March 19, 2010 11:59 AM
To: [email protected]
Subject: RE: Cla-Val # 581

Cal valve e-581 is field repairable. This valve has a very small seat area,
and any dirt or sand on the seat can cause it to leak. It must also use the
resilient seat not the metal to metal seat.
http://www.cla-val.com/fire-protection.cfm

Flushing the seat may clear it, without opening up the valve.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Doug Hicks
Sent: Friday, March 19, 2010 8:51 AM
To: sprinkler board
Subject: Cla-Val # 581

During an inspection, my tech found the FDC was full of water and was broken
at the top.  The FDC is a 90° Siamese double clapper rising out of the
ground. We are assuming the check valve is leaking. The check valve is a
Cla-Val # 581.  Is this valve repairable or should it be replaced?  The
building is only 4 years old.  What is the normal life of a valve like this?


Douglas Hicks
General Fire Equipment Co of Eastern Oregon, Inc
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to