Having personally built a number of "Pig Launchers" for PPG latex paint in
cheswold DE. In the 70's I can tell you that this is a labor intensive
activity, and not to be used except as a last resort. In these paint plants
the pigs were launched using HP compressed air, but you could use water. The
pigs were generally bullet shaped soft sponge with a plastic seat on the
compressed air end only .01" smaller than the ID of the pipe. The problem is
that even in these S.S. lines with full port BV the pigs occasionally became
stuck. The solution is to first backpressure the pig, and when that didn't
dislodge it you had to located the stoppage, and cut out that pipe section
to clear the pig. 

Now you're talking about doing this to underground! 

A PIG is hopefully a moveable obstruction and depending on your smallest
interior pipe dia. Only able to remove large blockages not scale,
tuberculosis or other pipe corrosion issues. Any corrosion will tend to jam
a pig.

Moving water at a reasonable rate has been the practice for a long time to
flush underground. Yes all of us have seen some weird stuff come out of that
underground during flushing. And have found weird stuff in BFP and riser
checks during inspections. But that is usually from failure to flush at all,
not from flushing at 8Fps or available flow.

The bigger question I have before wanting to make big changes to 24 is, what
is the system failure rate that would justify additional expense? What is
the current failure rate? How many fires have gone unchecked because of
stuff from the underground plugging heads valves or branch lines.

Too often we in the industry think in absolutes. ALL, SHALL, EVERY but the
insurance industry will tell you there are no absolutes! We will never be
perfect, our systems will never always work. And while it is cost effective
to get to 95% effective, to try and reach 96% could cost more than it did to
reach 95%.

Affordable effective protection is what we're after. We can save more lives
and property by spreading the existing protection available to 95% of the
population, than we can by improving the protection we give that small part
we call our customers.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


Subject: Re: Underground flushing velocities

Scott,

>From Wikipedia. Pigging can just be a single shot thing also. You just
drag the pig through a pipe not in use, then flush it.

Pigging
>From Wikipedia, the free encyclopedia


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to