Thanks Tom,
In this case the AHJ is letting us use LH.  Any thoughts on the 225 vs
130 spacing? 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tom
Duross
Sent: Friday, April 09, 2010 6:49 AM
To: [email protected]
Subject: RE: Unfinished basements in 4-family NFPA 13R occupancy

I use OH in residential basements, all steel and up through the floor,
then transition to plastic above the floor. 
Tom


I have a 4-family 13R (07ed) building with unfinished basements.  Please
confirm if my logic is on tract for sprinklering these areas.
For most AHJ's here, basements are not considered part of the dwelling
unit so they fall under section 6.8.2 - outside dwelling unit.
Only the design discharge and design area criteria from 13 apply so I
can sprinkler this area as LH with 225sf spacing no matter the type of
construction.  IE: I don't have to reduce the head spacing to 130sf
because of the TJI's 16" O.C.
Sound ok?
Thanks,
Dewayne Martinez

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to