Except in hospitals.  There are some doors in rated walls in healthcare 
occupancies that do not require a fire resistive rating.  Some do not require 
any hardware either.

Robert J. Pielow, P.E.



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Friday, April 09, 2010 1:03 PM
To: [email protected]
Subject: RE: rated walls, doors, hardware sets

1) Yes - 2006 IBC Section 715 - Table 715.4

2) Yes - 2006 IBC Section 715.4.7

Hope that helps,

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ed Kramer
Sent: Friday, April 09, 2010 1:41 PM
To: [email protected]
Subject: rated walls, doors, hardware sets

Here's a general question for the IBC savvy members:
 

If a wall is required to be 1 hr rated (or more), is it safe to assume doors
in the wall will have some level of fire rating?

Is it safe to assume doors in the wall will have self-closures?

 

We often have to work with architectural plans that are very much lacking in
details - to call them crappy is being kind.  I usually feel confident the
rated walls shown on the plan are accurate, but the door schedules
(including hardware sets) are too often an architectural afterthought. 

 

Thanks in advance,

Ed Kramer

Littleton, CO

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to