The ESFR exception is in 2002 Section 12.3.1.7.1(3) but not carried to 
12.4.1.1.1.   You could check the code change documentation to see if the 
change was viewed as a change in requirements or only a clarification that the 
ESFR exception that applies to other rack storage should also apply to tires.

Robert J. Pielow, P.E.
Fire Protection & Life Safety


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Fletcher, Ron
Sent: Tuesday, April 13, 2010 2:11 PM
To: [email protected]
Subject: Column Sprinklers in rubber tire storage

We have an AHJ that is using the 2002 NFPA 13 and doesn't care what is
in the 07. We have 25 ft. high tire storage in portable racks in a 35 ft
bldg. They want column sprinklers installed with the ESFR's because
there is no specific exception (that I can find) for column sprinklers
as there is in the 2007 Edition (18.2.4). There is not a bar in the
margin next to 18.2.4 so I was looking for the same language in the 02
but I cannot find. Hopefully I'm just missing it as usual. Anyone know
where it might be?

Ron Fletcher
Aero Automatic
Phoenix, AZ
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to