The ESFR exception is in 2002 Section 12.3.1.7.1(3) but not carried to 12.4.1.1.1. You could check the code change documentation to see if the change was viewed as a change in requirements or only a clarification that the ESFR exception that applies to other rack storage should also apply to tires.
Robert J. Pielow, P.E. Fire Protection & Life Safety -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Fletcher, Ron Sent: Tuesday, April 13, 2010 2:11 PM To: [email protected] Subject: Column Sprinklers in rubber tire storage We have an AHJ that is using the 2002 NFPA 13 and doesn't care what is in the 07. We have 25 ft. high tire storage in portable racks in a 35 ft bldg. They want column sprinklers installed with the ESFR's because there is no specific exception (that I can find) for column sprinklers as there is in the 2007 Edition (18.2.4). There is not a bar in the margin next to 18.2.4 so I was looking for the same language in the 02 but I cannot find. Hopefully I'm just missing it as usual. Anyone know where it might be? Ron Fletcher Aero Automatic Phoenix, AZ _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)