Don't assume that application of change to other rack storage will also apply 
to tires.  Tire protection is specific in the Standard.   


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Pielow, Robert
Sent: Tuesday, April 13, 2010 3:32 PM
To: [email protected]
Subject: RE: Column Sprinklers in rubber tire storage

The ESFR exception is in 2002 Section 12.3.1.7.1(3) but not carried to 
12.4.1.1.1.   You could check the code change documentation to see if the 
change was viewed as a change in requirements or only a clarification that the 
ESFR exception that applies to other rack storage should also apply to tires.

Robert J. Pielow, P.E.
Fire Protection & Life Safety


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Fletcher, Ron
Sent: Tuesday, April 13, 2010 2:11 PM
To: [email protected]
Subject: Column Sprinklers in rubber tire storage

We have an AHJ that is using the 2002 NFPA 13 and doesn't care what is in the 
07. We have 25 ft. high tire storage in portable racks in a 35 ft bldg. They 
want column sprinklers installed with the ESFR's because there is no specific 
exception (that I can find) for column sprinklers as there is in the 2007 
Edition (18.2.4). There is not a bar in the margin next to 18.2.4 so I was 
looking for the same language in the 02 but I cannot find. Hopefully I'm just 
missing it as usual. Anyone know where it might be?

Ron Fletcher
Aero Automatic
Phoenix, AZ
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to