If you use the longest length in your calcs and it works, then any shorter 
lengths will be known automatically to work.

Garth

----- Original Message ----- 
From: "George Medina Jr" <[email protected]>
To: <[email protected]>
Sent: Tuesday, April 20, 2010 2:41 AM
Subject: Calc Area


>
> If I am calculating a tree type system using the area/design method, and 
> have several different lengths between sprinklers on a branch line. Would 
> I use the longest length to determine the amount of
> sprinklers on a branch line. I have always used an average (which I've 
> probably been wrong all these years).
>
> 1.2√design area
>           S
> S= Distance between sprinklers on branch line
>
>
>
> 1.2√design area
>           S
> S= Distance between sprinklers on branch line
>
>
>
>
> George Medina Jr.
>
>