The length along the branch line, 1.2 x sq rt 1500 = 46.5' is measured from the wall (or center point between 2 spkrs) along the line, if it ends up mathmatically short of the center of two sprinklers you must pick up that additional sprinkler (end it at the center between the next head) and that "square " becomes the lengh S (be it 64') times L as a sq ft footprint, go to the next line and repeat, to the 46.5' and add those together, keep repeating until you reach 1500 sq ft, which will probably be more like 1640 or some such. If you want to really fine tune you can decrease the .1 density which is for the 1500 sq ft to the correct one for 1640
Tom Poisal, CET On Tue, Apr 20, 2010 at 10:58 AM, Ron Greenman <[email protected]>wrote: > And remember that FM is 1:1.4 suggesting that the adjusted ratio for > each entity has to be equal to or greater than 1: 1.2 (NFPA) or 1:1.4 > (FM). > > On Tue, Apr 20, 2010 at 7:54 AM, Brad <[email protected]> wrote: > > Something I overlooked until about 8 years ago: 1.2 x AREA USED--- > > Example 1500 SF- min. length 46.5', maybe 4 heads---- 1590 SF- min. > length > > 48', maybe 5 heads! > > > > -----Original Message----- > > From: Roland Huggins [mailto:[email protected]] > > Sent: Tuesday, April 20, 2010 9:36 AM > > To: [email protected] > > Subject: Re: Calc Area > > > > counting sprinklers is ONLY a casual means to check to ensure you are > > CLOSE to the required floor area. You must measure actual floor area > > with no regard to sprinkler spacing or distance to wall. Now in > > defining the area of coverage for each sprinkler, your question raises > > a point often asked. In a non-symmetrical layout, you use the longer > > on each side to define S and L such that the sprinkler is always in > > the center of the imaginary box. Not well explained by the standard > > since it mainly talks about distance to walls. > > > > Roland > > > > > > On Apr 19, 2010, at 11:41 PM, George Medina Jr wrote: > > > >> > >> If I am calculating a tree type system using the area/design method, > >> and have several different lengths between sprinklers on a branch > >> line. Would I use the longest length to determine the amount of > >> sprinklers on a branch line. I have always used an average (which > >> I've probably been wrong all these years). > >> > >> 1.2vdesign area > >> S > >> S= Distance between sprinklers on branch line > >> > >> > >> > >> 1.2vdesign area > >> S > >> S= Distance between sprinklers on branch line > >> > >> > >> > >> > >> George Medina Jr. > >> > >> > >> _______________________________________________ > >> Sprinklerforum mailing list > >> [email protected] > >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >> > >> For Technical Assistance, send an email to: [email protected] > >> > >> To Unsubscribe, send an email > to:[email protected]<to%[email protected]> > >> (Put the word unsubscribe in the subject field) > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > For Technical Assistance, send an email to: [email protected] > > > > To Unsubscribe, send an email > to:[email protected]<to%[email protected]> > > (Put the word unsubscribe in the subject field) > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > For Technical Assistance, send an email to: [email protected] > > > > To Unsubscribe, send an email > to:[email protected]<to%[email protected]> > > (Put the word unsubscribe in the subject field) > > > > > > -- > Ron Greenman > Instructor > Fire Protection Engineering > Bates Technical College > Tacoma, WA > > Member: > SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected]<to%[email protected]> > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)
