counting sprinklers is ONLY a casual means to check to ensure you are CLOSE to the required floor area. You must measure actual floor area with no regard to sprinkler spacing or distance to wall. Now in defining the area of coverage for each sprinkler, your question raises a point often asked. In a non-symmetrical layout, you use the longer on each side to define S and L such that the sprinkler is always in the center of the imaginary box. Not well explained by the standard since it mainly talks about distance to walls.
Roland On Apr 19, 2010, at 11:41 PM, George Medina Jr wrote: > > If I am calculating a tree type system using the area/design method, > and have several different lengths between sprinklers on a branch > line. Would I use the longest length to determine the amount of > sprinklers on a branch line. I have always used an average (which > I've probably been wrong all these years). > > 1.2√design area > S > S= Distance between sprinklers on branch line > > > > 1.2√design area > S > S= Distance between sprinklers on branch line > > > > > George Medina Jr. > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)