Doug, I am thinking about this way to much....me I would replace the valve
with a Nibco # F-910 flanged (wafer) check valve, it has the same 7.25"
takout, that unless you already ordered the rebuild kit..nibco seems a
simplier valve..just ma thought

On Sun, Apr 25, 2010 at 3:39 AM, Doug Hicks <[email protected]> wrote:

> I called ClaVal 3 times, finally the call was returned, but not by Cla Val.
> I did not understand the name, but I got the phone # right and called them
> back.  I specifically asked if this was a metal to metal or metal to rubber
> valve.  I was told It is supposed to be metal to metal, whichitis valve is.
> And the arrow is to the riser, but we are still getting water in the pipe
> from the FDC.  So, the check valve is leaking or the pipe is leaking and
> ground water is getting into the pipe.  I am going to go on the assumption
> the valve is leaking and needs a new clapper/gasket.
>
> --------------------------------------------------
> From: "tom poisal" <[email protected]>
> Sent: Saturday, April 24, 2010 7:59 PM
> To: <[email protected]>
> Subject: Re: Leak in FDC
>
> > Doug, now that you have set the situation right as it were, have you
> > pumped
> > (hydro'ed) the FDC to the cla val? and have you made sure it is not
> > installed backwards......arrrow towards the riser, and I noticed the
> > detail
> > "opitional seating metal to buna-n" on the pdf,  I know your ina hole but
> > this could be your loss..in a nut shell he he
> >
> >
> >
> >
> > On Sat, Apr 24, 2010 at 9:33 PM, Doug Hicks <[email protected]> wrote:
> >
> >> The FDC is in the yard of a drug and alcohol treatment center.  Yes, the
> >> cement covered pipe is the underground from the FDC to the pit with the
> >> sprinkler line to the builidng.
> >>
> >> I am not sure if we havhole in the underground piping or not.  I want to
> >> try other remedies before digging a 5 foot hole in the ground .
> >>
> >> We drilled a hole in the pipe for a ball drip because
> >> 1. There is no provision for a ball drip valve in the 581 Cla Val check
> >> valve.
> >> 2. All of the FDC piping I have seen has a ball drip valve
> >> 3. NFPA 13-2007 Figure A.8.17.2(b) shows a ball drip
> >>
> >> --------------------------------------------------
> >> From: "Matt Grise" <[email protected]>
> >> Sent: Thursday, April 22, 2010 5:31 AM
> >> To: <[email protected]>
> >> Subject: RE: Leak in FDC
> >>
> >> > Doug,
> >> >
> >> > Just to clarify:
> >> >
> >> > This is a remote FDC? The cement covered pipe is the underground run
> >> > from
> >> > the building to the remote FDC? The problem is water leaking out of
> the
> >> > FDC hose connections?
> >> >
> >> > Also:
> >> > Why did you drill a hole in the cement covered pipe?
> >> >
> >> > Matt Grisé PE*, LEED AP
> >>
> >> > Subject: Leak in FDC
> >> >
> >> > We are still having problems with an FDC leaking.  We replaced the
> FDC,
> >> > removed the ClaVal 581 check valve and cleaned it.  We drilled a 2"
> >> > hole
> >> > in a cement covered pipe and found  one hole  drilled is the life span
> >> > of
> >> > the hole saw.  Drilling the pipe makes a horrible noise also.
> >> >
> >> > But we still have water being introduced into the underground pipe.
> >> > The
> >> > cement covered pipe screws into a 4 inch galvanized pipe that exits
> >> > vertically from the ground.  We could have a leaking 581 valve, we
> >> > could
> >> > have a leak in the pipe and are having ground water forced into the
> >> > pipe.
> >>
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email
> >> to:[email protected]<to%[email protected]>
> <to%[email protected]<to%[email protected]>
> >
> >> (Put the word unsubscribe in the subject field)
> >>
> >
> >
> >
> > --
> > Tom Poisal, CET
>  > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> > (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>



-- 
Tom Poisal, CET
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to