there was a FPRF project back in 2006 that looked at Mercantile  
occupancies using Gondola shelves with OHGII protection.  I know one  
of the test was Group A plastic at 12 ft and 4 ft aisles.  As soon as  
it jumped that narrow 4 ft aisle, it took very little time to run  
away.  That fire was rockin'.

Roland

On Apr 28, 2010, at 7:30 AM, [email protected] wrote:

> I am doing research to write a report for our Client on protecting  
> Group A
> plastics displayed on Gondolas (display shelves in a store, 2010  
> NFPA 13
> Section 20.3.3).  The Client is currently being asked to protect these
> areas with a density of .45 gpm/ft2 over an area of 2,000 square feet.
>
> I am trying to find some UL/FM/other test data that shows sprinklers  
> using
> lower densities (lower than .45/2000) able to control a fire with  
> Group A
> plastics displayed on gondolas (open shelf displays apx. 8 ft tall).
>
> Any ideas?  Help?
>
> Sue Stafford, S.E.T. | Associate Designer
> SCHIRMER ENGINEERING an Aon Global company
> Texas P.E. Firm Registration No. F-1593
> 1701 N. Collins Blvd., Suite 235
> Richardson, TX 75080
> Tel: 972.234.1617 | Fax: 972.234.2753| Direct: 214.414.1264
> e-mail: [email protected]
> website: http://www.schirmereng.com/
> Fire Protection  n  Code Consulting  n  Risk Assessment  n  Process
> Safety  n  Security Consulting
> P Please consider the environment before printing this e-mail.
> NOTICE: This message may contain information that is privileged and/or
> confidential and is intended for the sole use of the intended  
> recipient.
> If you are not the intended recipient or a person responsible for
> delivering it thereto, you may not disclose, use, disseminate,  
> distribute,
> copy or take any action in reliance on this message or any attachments
> thereto in any way. If you have received this message in error, please
> return it by forwarding the message and all attachments to the sender.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to