Susan, time to pull out the good book. Look at 2010 NFPA 13 chapter 15,
specifically Table 15.2.2.

For back to back shelf storage of cartooned unexpanded group A plastics.

Ceilings of less than 30'-0"

Over 5'-0" up to 8'-0" OHII
Up to 15'-0" 0.7/2500

Remember that if your top shelf is at 8'-0" they will store above that, so
then your 8'-0" storage is actually 10 or 11'-0" and your required design
goes to .45/2500

All of this is based upon the Fire Protection Research Foundation study of
"Evaluation of sprinkler performance in protecting Gondola type shelf
storage" 


Thom McMahon, SET
Firetech, Inc.