I don't think you are going to shoe-horn this into Misc. storage since shelving 
of commodities for sale is the primary function of the occupancy.

Since it's impractical and most times impossible to provide in-rack protection 
you are pretty much forced to use the increased discharge criteria based on 
ceiling sprinklers only.

So .45 over 2000 isn't necessarily out of line for this type of hazard.

And BTW, this is a mercantile occupancy.



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, April 28, 2010 11:03 AM
To: [email protected]
Subject: Research Question - Group A Plastic Protection

Primarily the storage is:

exposed in cardboard boxes
majority are unexpanded
unencapsulated
shelving is solid

The client is asking to consider as Miscellaneous storage


Sue Stafford, S.E.T. | Associate Designer
SCHIRMER ENGINEERING an Aon Global company
Texas P.E. Firm Registration No. F-1593
1701 N. Collins Blvd., Suite 235
Richardson, TX 75080
Tel: 972.234.1617 | Fax: 972.234.2753| Direct: 214.414.1264
e-mail: [email protected]
website: http://www.schirmereng.com/
Fire Protection  n  Code Consulting  n  Risk Assessment  n  Process 
Safety  n  Security Consulting
P Please consider the environment before printing this e-mail.
NOTICE: This message may contain information that is privileged and/or 
confidential and is intended for the sole use of the intended recipient. 
If you are not the intended recipient or a person responsible for 
delivering it thereto, you may not disclose, use, disseminate, distribute, 
copy or take any action in reliance on this message or any attachments 
thereto in any way. If you have received this message in error, please 
return it by forwarding the message and all attachments to the sender.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to