I'll take a stab. Based on my visual of the room, I would grab 900 sq ft that picks up the 4 ex cov sprinklers and 1 of the SSP's.
On 4/30/2010 11:15 AM, Vince Sabolik wrote: > Good afternoon (anyone working this late) > > I have a classroom about 1,230 sq ft. > > In it are 4 extended coverage heads and due to wall abberations, > 4 standard heads. The extended heads are spaced at 18 x 18. > > The room is enclosed by rated construction and the ceiling's 9-0. > > How many heads would YOU include in the calcs? > > thanks, Vince > > Vince Sabolik > Christi Fire Protection, Inc. > 11351 Pearl Road > Strongsville, Ohio 44136 > > T 440 572-7730 F 440 572-7719 Email: > <mailto:[email protected]>[email protected] > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)