I'll take a stab.  Based on my visual of the room, I would grab 900 sq 
ft that picks up the 4 ex cov sprinklers and 1 of the SSP's.

On 4/30/2010 11:15 AM, Vince Sabolik wrote:
> Good afternoon (anyone working this late)
>
> I have a classroom about 1,230 sq ft.
>
> In it are 4 extended coverage heads and due to wall abberations,
> 4 standard heads. The extended heads are spaced at 18 x 18.
>
> The room is enclosed by rated construction and the ceiling's 9-0.
>
> How many heads would YOU include in the calcs?
>