Thanks for the help.

Prior to my request, using the QR reduction, I had calculated
six heads. This settled a friendly argument.

                                                        thanks! Vince



At 02:15 PM 4/30/2010, you wrote:
>Good afternoon (anyone working this late)
>
>I have a classroom about 1,230 sq ft.
>
>In it are 4 extended coverage heads and due to wall abberations,
>4 standard heads. The extended heads are spaced at 18 x 18.
>
>The room is enclosed by rated construction and the ceiling's 9-0.
>
>How many heads would YOU include in the calcs?
>
>                                                              thanks, Vince
>