Assuming all sprinks are rated QR (including the EC's at 18' x 18'): the most demanding 900 sf, but not less than 5 sprinklers.
The most demanding 900 sf may be the 4 EC's plus 1 or more SC's. Or it may be 3 EC's plus 2 or more SC's. Regardless, it needs to be the most demanding 900 sf (but not less than 5 sprinks). Ed Kramer Littleton, CO > -----Original Message----- > From: [email protected] [mailto:sprinklerforum- > [email protected]] On Behalf Of Vince Sabolik > Sent: Friday, April 30, 2010 12:15 PM > To: [email protected] > Subject: HEAD COUNT > > Good afternoon (anyone working this late) > > I have a classroom about 1,230 sq ft. > > In it are 4 extended coverage heads and due to wall abberations, > 4 standard heads. The extended heads are spaced at 18 x 18. > > The room is enclosed by rated construction and the ceiling's 9-0. > > How many heads would YOU include in the calcs? > > thanks, > Vince > > Vince Sabolik > Christi Fire Protection, Inc. > 11351 Pearl Road > Strongsville, Ohio 44136 > > T 440 572-7730 F 440 572-7719 Email: > <mailto:[email protected]>[email protected] > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:Sprinklerforum- > [email protected] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)