sam,  it is the temp rise/loss; when it gets to night time the water cools
and lowers the temp which lowers the psi/bar same with an overnight hydro
test..not much you can do about it that i know.


On Mon, May 3, 2010 at 2:57 PM, sam b <[email protected]> wrote:

> Hii  everyone
>
>
> My previos mail in this forum was regarding a temporary fire pump(only
> dieselPump) only.
> we have installed this fire pump for temporary fire fighting in  the site.
> The pump is 500 USGpm @ 20 Bar.(NOn Listed).The risers we have installed up
> to 7 floors now.
> The pressure switch setting is kept such that when presuure drops below 16
> Bar the pump automatically starts.
> For the last 2 days we are seeing that the pump starts automatically at
> night time.In the daytime there is no considerable pressure loss also.
> our initial assesment was that it may due to air trapped inside ,as a
> result
> we installed air release valve in both risers .Also the NRV in the
> pumpdiischarge was replaced to ensure there is no leakage.
>
> Any guesses on whtmay b the reason?
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>



-- 
Tom Poisal, CET
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to