Tom, look at your conversion factor again.  Bar X 14.5 = psi.

Pump rating is 20 bar (290 psi), set point to start is 16 bar (232 psi).

You're saying there is a system pressure differential of 4 bar (58 psi) between 
normal daytime pressure and night time pressures?

Apparently you don't have a jockey pump on the system to maintain the pressure? 
 

Any reason not to adjust the differential a bit wider, say drop the start point 
to 14 bar maybe?

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of tom poisal
Sent: Monday, May 03, 2010 3:18 PM
To: [email protected]
Subject: Re: Fire Pump

On Mon, May 3, 2010 at 3:08 PM, sam b <[email protected]> wrote:

> but do you expect this to go down so much ,more than 2 bars even,.?
> am actually  waiting for the status tonight...:)
>
> Yeah your talking 2 bars = only .1378 psi, I have seen systems lose 5-6 psi
> overnight and gain it when the sun rises
>
> On Mon, May 3, 2010 at 11:02 PM, tom poisal <[email protected]> wrote:
>
> > sam,  it is the temp rise/loss; when it gets to night time the water
> cools
> > and lowers the temp which lowers the psi/bar same with an overnight hydro
> > test..not much you can do about it that i know.
> >
> >
> > On Mon, May 3, 2010 at 2:57 PM, sam b <[email protected]> wrote:
> >
> > > Hii  everyone
> > >
> > >
> > > My previos mail in this forum was regarding a temporary fire pump(only
> > > dieselPump) only.
> > > we have installed this fire pump for temporary fire fighting in  the
> > site.
> > > The pump is 500 USGpm @ 20 Bar.(NOn Listed).The risers we have
> installed
> > up
> > > to 7 floors now.
> > > The pressure switch setting is kept such that when presuure drops below
> > 16
> > > Bar the pump automatically starts.
> > > For the last 2 days we are seeing that the pump starts automatically at
> > > night time.In the daytime there is no considerable pressure loss also.
> > > our initial assesment was that it may due to air trapped inside ,as a
> > > result
> > > we installed air release valve in both risers .Also the NRV in the
> > > pumpdiischarge was replaced to ensure there is no leakage.
> > >
> > > Any guesses on whtmay b the reason?
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > For Technical Assistance, send an email to: [email protected]
> > >
> > > To Unsubscribe, send an email
> > to:[email protected]<to%[email protected]>
> <to%[email protected]<to%[email protected]>
> >
> > <to%[email protected]<to%[email protected]>
> <to%[email protected]<to%[email protected]>
> >
> > >
> > > (Put the word unsubscribe in the subject field)
> > >
> >
> >
> >
> > --
> > Tom Poisal, CET
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> <to%[email protected]<to%[email protected]>
> >
> > (Put the word unsubscribe in the subject field)
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>



-- 
Tom Poisal, CET
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to