craig Surely that can be done.(adjust the differential) But am worried what is goin wrong?
On Mon, May 3, 2010 at 11:23 PM, <[email protected]> wrote: > Tom, look at your conversion factor again. Bar X 14.5 = psi. > > Pump rating is 20 bar (290 psi), set point to start is 16 bar (232 psi). > > You're saying there is a system pressure differential of 4 bar (58 psi) > between normal daytime pressure and night time pressures? > > Apparently you don't have a jockey pump on the system to maintain the > pressure? > > Any reason not to adjust the differential a bit wider, say drop the start > point to 14 bar maybe? > > Craig L. Prahl, CET > Fire Protection Specialist > Mechanical Department > CH2MHILL > Lockwood Greene > 1500 International Drive > Spartanburg, SC 29304-0491 > Direct - 864.599.4102 > Fax - 864.599.8439 > [email protected] > http://www.ch2m.com > > > -----Original Message----- > From: [email protected] [mailto: > [email protected]] On Behalf Of tom poisal > Sent: Monday, May 03, 2010 3:18 PM > To: [email protected] > Subject: Re: Fire Pump > > On Mon, May 3, 2010 at 3:08 PM, sam b <[email protected]> wrote: > > > but do you expect this to go down so much ,more than 2 bars even,.? > > am actually waiting for the status tonight...:) > > > > Yeah your talking 2 bars = only .1378 psi, I have seen systems lose 5-6 > psi > > overnight and gain it when the sun rises > > > > On Mon, May 3, 2010 at 11:02 PM, tom poisal <[email protected]> wrote: > > > > > sam, it is the temp rise/loss; when it gets to night time the water > > cools > > > and lowers the temp which lowers the psi/bar same with an overnight > hydro > > > test..not much you can do about it that i know. > > > > > > > > > On Mon, May 3, 2010 at 2:57 PM, sam b <[email protected]> wrote: > > > > > > > Hii everyone > > > > > > > > > > > > My previos mail in this forum was regarding a temporary fire > pump(only > > > > dieselPump) only. > > > > we have installed this fire pump for temporary fire fighting in the > > > site. > > > > The pump is 500 USGpm @ 20 Bar.(NOn Listed).The risers we have > > installed > > > up > > > > to 7 floors now. > > > > The pressure switch setting is kept such that when presuure drops > below > > > 16 > > > > Bar the pump automatically starts. > > > > For the last 2 days we are seeing that the pump starts automatically > at > > > > night time.In the daytime there is no considerable pressure loss > also. > > > > our initial assesment was that it may due to air trapped inside ,as a > > > > result > > > > we installed air release valve in both risers .Also the NRV in the > > > > pumpdiischarge was replaced to ensure there is no leakage. > > > > > > > > Any guesses on whtmay b the reason? > > > > _______________________________________________ > > > > Sprinklerforum mailing list > > > > [email protected] > > > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > > > > For Technical Assistance, send an email to: > [email protected] > > > > > > > > To Unsubscribe, send an email > > > to:[email protected]<to%[email protected]> > <to%[email protected]<to%[email protected]> > > > > <to%[email protected]<to%[email protected]> > <to%[email protected]<to%[email protected]> > > > > > > > > <to%[email protected]<to%[email protected]> > <to%[email protected]<to%[email protected]> > > > > <to%[email protected]<to%[email protected]> > <to%[email protected]<to%[email protected]> > > > > > > > > > > > > > (Put the word unsubscribe in the subject field) > > > > > > > > > > > > > > > > -- > > > Tom Poisal, CET > > > _______________________________________________ > > > Sprinklerforum mailing list > > > [email protected] > > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > > For Technical Assistance, send an email to: [email protected] > > > > > > To Unsubscribe, send an email > > to:[email protected]<to%[email protected]> > <to%[email protected]<to%[email protected]> > > > > <to%[email protected]<to%[email protected]> > <to%[email protected]<to%[email protected]> > > > > > > > > (Put the word unsubscribe in the subject field) > > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > For Technical Assistance, send an email to: [email protected] > > > > To Unsubscribe, send an email > to:[email protected]<to%[email protected]> > <to%[email protected]<to%[email protected]> > > > > (Put the word unsubscribe in the subject field) > > > > > > -- > Tom Poisal, CET > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected]<to%[email protected]> > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected]<to%[email protected]> > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)