Eric,

Why not look at using the room design method for OH - 11.2.3.3.5 (3).  As
long as you meet all of the requirements this is a simpler alternative. 

Cliff Whitfield, SET
President
Fire Design, Inc.

[email protected]
www.fire-design.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Shelton, Eric
Sent: Tuesday, May 11, 2010 10:53 AM
To: [email protected]
Subject: Multiple adjustments to remote area

How are multiple adjustments made to a remote area that includes a 700
sf mechanical room (OH2) with a 2.5:12 sloped ceiling greater than 20'
high that is surrounded by offices (LH) with 10' level ceilings?  The
mechanical room that is separated from the rest of the building by
non-rated, but smoke-resistant, walls.

 

I'm thinking it would be reasonable to use all 700 sf of the mech room
but reduce the other 2300 sf by 40%, making 700 + (0.6)(2300) = 2080 sf.
Since only the mech room ceiling is sloped it doesn't make sense to
apply an increase to the entire area.

 

I know I have to use the higher hose stream and duration per 11.1.5.2
because my higher density area is over 400 sf.

 

Eric J. Shelton, PE

Senior Fire Protection Engineer

AECOM Design

Direct 540.857.3282

AECOM

10 South Jefferson Street, Suite 1600

Roanoke, Virginia 24011
T 540.857.3100   F 540.857.3180

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to