Apples and Oranges.  A building can be deemed Hazardous because of
non-fire related hazards (like H-4 for corrosive, toxic, or highly toxic
materials).  The IBC and NFPA 13 are two different codes with very
different ways of classifying the hazards.  One is for the building, the
other is for the sprinkler system.  While the NFPA 13 standard is
looking at addressing a fire hazard [quantity and combustibility of
contents, etc.] the IBC standard is classifying the occupancy based on
many other factors related to human safety in general.  The number of
occupants, the age of occupants, the ability of occupants to evacuate
during an emergency, whether people sleep there, the duration people
stay in the building, the quantity and nature of buildings contents,
etc.

 

When I get an engineer who completes our Fire Sprinkler System
Specification Sheet form
[http://www.llr.state.sc.us/FMARSHAL/EngServices/index.asp?file=forms.ht
m] with an IBC occupancy class even though we have purposely labeled the
form section as "NFPA Hazard Classification", it is a  BIG RED FLAG that
the engineer may be practicing outside their area of expertise...  If
the plans they have either sealed or certified compliant also show
evidence of practicing outside their area of expertise it can require us
to refer them to the Engineering Board.  

 

We are a general practice state with regards to engineers so we can't
require they pass a specific PE test like fire protection to demonstrate
competence and we don't require a resume of experience becuase the
assumption is they will know and obey their licensing law.  PEs licensed
in SC are required by SC to self-regulate and not practice outside their
area of expertise.  Unfortunately, that is enough slack rope for some to
hang themselves with by taking on projects that they are not
sufficiently competent for...

 

I've not yet encountered a licensed sprinkler contractor with a NICET IV
completing our form [per 40-10-250(B) of
http://www.scstatehouse.gov/code/t40c010.htm] who has caused me to issue
a similar competence referral [under their licensing statute].

 

 

 

David W. S. Blackwell, II, PE, CFI-I, CFPE

Engineering 

---------------------------------------------------------------- 

Office of State Fire Marshal 

141 Monticello Trail 

Columbia, SC 29203 

Phone:  803.896.9833 

Fax:  803.896.9806 

Email:  [email protected] 

OSFM Website: http://www.llr.state.sc.us/firemarshal.asp 

---------------------------------------------------------------- 

 

 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Fletcher,
Ron
Sent: Wednesday, May 26, 2010 4:53 PM
To: [email protected]
Subject: Occupancy vs Hazard

 

Is there a correlation between the IBC occupancy and NFPA #13 Hazard? I

have a set of plans where the building occupancy classification is H-1

and the EOR has specified OH-II for the sprinkler system. I have always

thought (maybe mistakenly) that any H occupancy would be EH-I minimum.

 

Ron Fletcher

Aero Automatic

Phoenix, AZ

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 

For Technical Assistance, send an email to: [email protected]

 

To Unsubscribe, send an email
to:[email protected]

(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to