Dear Craig,

Thanks so much for your comments, appreciate your support.

Kin Regards,


César

 

________________________________
From: "[email protected]" <[email protected]>
To: [email protected]
Sent: Mon, June 7, 2010 8:22:43 AM
Subject: RE: HANGAR BUILDING - DELUGE TANK

We have one client which requires foam-water discharge be captured.  It is 
retained and then after the event it is pumped into tanker trucks and hauled 
off.  You need to check with the owner or local environmental authorities to 
see if that is required.  If available, an alternative to hauling off the waste 
water is to release it to a municipal sewer or to a process sewer.

I'm assuming that by your mention of a retention tank that you are providing 
drains in the hangar and piping them to this tank?

Here is one problem.  For a foam-water sprinkler system to properly work on 
suppressing or controlling a pool fire, the foam must be able to remain on top 
of the spilled fuel.  If you drain it off as fast as it comes out of the 
sprinkler heads then it may not perform as intended.  

If the foam-water discharge is contained within the hangar, it can be routed to 
a low point sump within the hangar and then under controlled conditions allowed 
to discharge to a remote holding tank to be carried off in a tanker truck or to 
be released into a sewer system.

When we have been required to provide drains they are undersized so that the 
foam has time to settle on the fuel before draining off.  We have also had 
clients with special, valved drains for this same purpose.  There are all kinds 
of ways to deal with this situation.  

There are many ways to retain the sprinkler discharge, either in a concrete 
underground tank, a lined retention pond, remote holding area, etc.  Piping to 
these is basic plumbing design, nothing special.  Just make sure the piping is 
suitable for the material that will be running through it.

If there is any uncertainty on how to design this system I would suggest you 
contact a qualified mechanical and civil engineer for assistance.  



Craig L. Prahl, CET  
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of César 
Villavicencio
Sent: Sunday, June 06, 2010 3:27 PM
To: [email protected]
Subject: HANGAR BUILDING - DELUGE TANK

Dear Forum Members,
 
I do need from your experience on the design of foam water systems regarding 
the handling of waste water.
 
There is a hangar in construction but we have no clue of how to design the 
plumbing system for a 2000m3 Deluge Holding / Retention Tank.
 
There are no specific mechanical / piping details for the 2000m3 Retention Tank 
and how the waste (contaminated) water is taken care of. 
 
We would deeply appreciate any input to solve this issue.
 
We look forward to hearing from you.
 
 
Kind Regards,



Cesar Villavicencio 


      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to