I have a 2000 GPM pump and per NFPA 20 Table 5.25(a) the Suction and Discharge piping is to be 10". I understand the suction piping has to be 10" for a minimum of 100" (10x the pipe diameter), but how long do I have to keep the discharge pipe 10" before I can reduce to the 8" UG connection?
Thank you, Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)