He was asking about Suction pipe sizing.

On 6/10/2010 8:29 AM, Travis Mack, SET wrote:
> NFPA 20 ends at the pump discharge valve.  You can reduce after that.
>
> On 6/10/2010 8:25 AM, Bobby Gillett wrote:
>    
>> I have a 2000 GPM pump and per NFPA 20 Table 5.25(a) the Suction and
>> Discharge piping is to be 10". I understand the suction piping has to be 10"
>> for a minimum of 100" (10x the pipe diameter), but how long do I have to
>> keep the discharge pipe 10" before I can reduce to the 8" UG connection?
>>
>>
>>
>> Thank you,
>>
>>
>>
>> Bobby Gillett
>>
>> Sr. Project Manager
>>
>> Key Fire Protection, Inc.
>>
>> (731) 424-0130 office  (731) 424-9285 fax
>>
>> (731) 267-4853 cell
>>
>>    <mailto:[email protected]>
>> [email protected]
>>
>>
>>
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>>      
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>    

-- 
Greg McGahan
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to