100"

On 6/10/2010 8:25 AM, Bobby Gillett wrote:
> I have a 2000 GPM pump and per NFPA 20 Table 5.25(a) the Suction and
> Discharge piping is to be 10". I understand the suction piping has to be 10"
> for a minimum of 100" (10x the pipe diameter), but how long do I have to
> keep the discharge pipe 10" before I can reduce to the 8" UG connection?
>
>
>
> Thank you,
>
>
>
> Bobby Gillett
>
> Sr. Project Manager
>
> Key Fire Protection, Inc.
>
> (731) 424-0130 office  (731) 424-9285 fax
>
> (731) 267-4853 cell
>
>   <mailto:[email protected]>
> [email protected]
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>    

-- 
Greg McGahan
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to