I agree with the concept, but how far would you go? The collapse affected parts of 2 systems but there are 16 systems in this building. Would you make an argument that the adjoining sprinkler systems were also affected? Should it be based on the distance from the collapsed section or the sprinkler piping layout?
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Chris Cahill Sent: Tuesday, June 22, 2010 4:40 PM To: [email protected] Subject: RE: Rebuilidng a sprinkler system after a partial roof collapse With the cost of heads being relatively cheap it's not even a question in my mind - replace them. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of David Bitton Sent: Tuesday, June 22, 2010 3:37 PM To: 'Sprinkler Forum' Subject: Rebuilidng a sprinkler system after a partial roof collapse Hello all, A 14,000 sq. ft. section of a large warehouse collapsed, bringing down some sprinkler piping that will need to be replaced. I am concerned that the operating elements on the remaining sprinkler heads have been weakened by the pipe movement during the collapse and would fail once we do the hydrostatic test on the system, causing water damage to the stock. Are there any guidelines for determining whether the remaining heads need to be replaced? (A visual inspection revealed no apparent damage to these heads.) Thanks, David Bitton, Eng. Quest Loss Control Services Inc. Les services de prévention des sinistres Quest inc. 5100, rue de la Savane, bureau 200 Montréal, QC H4P 1T8 (514) 341-4545 www.questlosscontrol.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)