Greg, This is similar in nature to a "downdraft" paint spray booth with spklrs. in the booth and in the pit /tunnels below the floor/filter media.I calc'd the roof as an area,then the booth and pit with heads flowing in both areas.You may need to do likewise in this case.JMHO
Lamar Vaughn,SET ---- Greg McGahan <[email protected]> wrote: > Trying to calc a recycling sorting facility buildout - there is a small > "hut" in the center where the sorting takes place and holes in the floor > (approx 3-6 x 2-6) with bins underneath for the sorted materials. > Therefore there is protection at the roof of the building, at the roof > of the "hut" and under the floor of the hut. > > Technically speaking, we can calc one level of protection, but my > question is for those who may have experience with these, should we calc > the lower level and include some heads inside the hut on the chance that > the fire could come through the holes in the floor to the interior of > the hut? > > Thanks > -- > Greg McGahan > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)