Greg,
 This is similar in nature to a "downdraft" paint spray booth with spklrs. in 
the booth and in the pit /tunnels below the floor/filter media.I calc'd the 
roof as an area,then the booth and pit with heads flowing in both areas.You may 
need to do likewise in this case.JMHO

Lamar Vaughn,SET

  
---- Greg McGahan <[email protected]> wrote: 
> Trying to calc a recycling sorting facility buildout - there is a small 
> "hut" in the center where the sorting takes place and holes in the floor 
> (approx 3-6 x 2-6) with bins underneath for the sorted materials. 
> Therefore there is protection at the roof of the building, at the roof 
> of the "hut" and under the floor of the hut.
> 
> Technically speaking, we can calc one level of protection, but my 
> question is for those who may have experience with these, should we calc 
> the lower level and include some heads inside the hut on the chance that 
> the fire could come through the holes in the floor to the interior of 
> the hut?
> 
> Thanks
> -- 
> Greg McGahan
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to