Dewayne,

Yes, the site class is one of the first steps in a process to determine 
the seismic design category, based on the procedure in ASCE7-05.

If you end up in seismic design category A or B, ASCE7-05 has no 
information on requirement for seismic bracing.

If you end up in seismic design category C, ASCE7-05 requires that you 
provide seismic protection in accordance with the '02 edition of -13.

If you end up in seismic design category D-E-F, ASCE7-05 requires that 
you provide seismic protection in accordance with the '02 edition of 
-13, and take into account the strength of the mains, and the horizontal 
force factors as noted in ASCE7-05.  You are deemed to have met the 
latter requirement if you follow the 2007 NFPA-13 guidelines, or the 
2010 NFPA-13 guidelines.

Clear as mud, right?

insert NFPA committee member disclaimer and so forth....
-- 
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website



Dewayne Martinez wrote:
> Is the site class used to determine the design category?
>  
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Thursday, June 24, 2010 4:00 PM
> To: [email protected]
> Subject: RE: seismic design category
>
> Design category is your deciding factor.  For an "A" category you should have 
> to do nothing special.  
>
> But, a few years ago we had a similar situation with concrete anchors so it 
> could be an owner standard requirement not necessarily based on seismic 
> issues.
>
> Craig L. Prahl, CET   
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com 
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Dewayne 
> Martinez
> Sent: Thursday, June 24, 2010 4:55 PM
> To: [email protected]
> Subject: seismic design category
>
> What is the difference between the "seismic site class" and the "seismic 
> design category"?
> I have an engineer who is making us install "cracked concrete approved"
> inserts based upon
> a seismic site class C.  The structural drawings also show a seismic design 
> category A.
> I thought that the design category is what we use to determine if seismic 
> hangers are required?
> Here is Wisconsin we don't see this so this I am a bit confused.
> Thanks,
> Dewayne
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to