pardon let me add the second negative:  NOT rent if system can NOT  
adequately protect actual contents

Roland

On Jul 14, 2010, at 7:27 AM, Roland Huggins wrote:

> Same answer as the Haunted house and Rain Forest Cafe, you go on what
> is actually or intended to be present in accordance with the
> definitions of 13.  Self storage could be ch 13 depending on contents
> and height (Class I-IV to 12 ft but Group A plastics only 5 ft).
>
> Granted many spec storage areas use OH2 but that actual means you are
> not SUPPOSE to rent the space if the occupant intends to store what
> the system is capable of protecting (lets all hold our breath waiting
> on that approach).
>
> Roland
>
>
> On Jul 14, 2010, at 6:39 AM, Matthew J. Willis wrote:
>
>> For some reason I cannot get to the archives. 42,000 Sq. Ft. of self
>> storage
>> units, with wire across the top at 8'-0". I was thinking Class IV,
>> but I
>> seem to remember some discussion previously. Am I remembering
>> correctly?
>>
>>
>>
>> Thanks,
>>
>>
>>
>> Matt
>>
>>
>>
>>
>>
>> Matthew J. Willis, CET
>>
>> Automatic Fire Sprinklers
>>
>> Norred Fire Systems L.L.C.
>>
>> 318-387-1134 Voice
>>
>> 318-816-1087 Mobile
>>
>> 318-387-1163 Facsimile
>>
>> [email protected]
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to