Scenario:             3-story Light Hazard (Residential) occupancy,
fully sprinklered per 13.

Situation:             Exterior exit stairs are too close to glazed
openings in exterior walls and 45-minute window protection is required
(from inside out) for several 2'x3' fixed windows on all three floors.

Challenge:           Can't use window sprinklers because exterior walls
are bearing.   Am proposing to use water curtain provisions of the
building code, and furnish 3 GPM per lineal foot per 13.

 

Question:            Since the windows are only 2' wide, and there are
up to 3 windows in a cluster, we will have sprinklers at 4' apart in
several areas and will be provided a baffle of some sort.    I can
easily hit my minimum flow rate with small orifice sprinklers and do not
see any restriction in 13 regarding orifice size in a water curtain.
Since it's all Light Hazard, can anyone think of a reason why we can't
use 4.2K pendents?

 

Steve Leyton

PROTECTION DESIGN & CONSULTING