The AHJ wants additional protection, to mitigate fire spread from the
interior toward exterior stairs in proximity to the affected openings.
The building code allows for protection of openings in a fully
sprinklered building by use of a water curtain per 903.3.1.1, i.e. NFPA
13.   We're going to cobble together the discharge criteria and
placement of a sprinkler over the interior side of each panel and call
it a day.  I don't write the copy, just reading the news into the
camera.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mike
Hairfield
Sent: Thursday, July 15, 2010 12:22 PM
To: AFSA SprinklerFORUM
Subject: RE: Small Orifice Sprinklers in Water Curtain


Shouldn't you be looking at Exposure Protection Sprinkler Systems which
allows different

K factors?

 

Mike
 
> Subject: Small Orifice Sprinklers in Water Curtain
> Date: Thu, 15 Jul 2010 12:12:11 -0700
> From: [email protected]
> To: [email protected]
> 
> Scenario: 3-story Light Hazard (Residential) occupancy,
> fully sprinklered per 13.
> 
> Situation: Exterior exit stairs are too close to glazed
> openings in exterior walls and 45-minute window protection is required
> (from inside out) for several 2'x3' fixed windows on all three floors.
> 
> Challenge: Can't use window sprinklers because exterior walls
> are bearing. Am proposing to use water curtain provisions of the
> building code, and furnish 3 GPM per lineal foot per 13.
> 
> 
> 
> Question: Since the windows are only 2' wide, and there are
> up to 3 windows in a cluster, we will have sprinklers at 4' apart in
> several areas and will be provided a baffle of some sort. I can
> easily hit my minimum flow rate with small orifice sprinklers and do
not
> see any restriction in 13 regarding orifice size in a water curtain.
> Since it's all Light Hazard, can anyone think of a reason why we can't
> use 4.2K pendents?
> 
> 
> 
> Steve Leyton
> 
> PROTECTION DESIGN & CONSULTING
> 
> 2851 Camino del Rio South, Suite 400
> 
> San Diego, CA 92108
> 
> -------------------------------------------------------------
> 
> Ph: 858.751.2930 - ext. 102
> 
> Fax: 858.751.2933
> 
> Cell: 619.972.5696
> 
> 
> 
> 
> 
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 5282 (20100715) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 5282 (20100715) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to