The exception to 704.12 to allow a water curtain in lieu of fire protected 
glazing is simply odd when the curtain is only required on the inside of the 
building.

The implication is that fire sprinklers in a fully sprinklered building are not 
sufficient to prevent a room fire from busting out a window and spreading 
across the exterior walls (or through space) to the stair that is 10 ft. away.  
I suppose it could happen, but seems like a low probability event if the 
sprinklers are in service.  If the sprinks are out of service good chance the 
water curtain is as well.

Rich Richardson
Seattle Fire Department

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Thursday, July 15, 2010 13:25
To: [email protected]
Subject: RE: Small Orifice Sprinklers in Water Curtain

We're using 704.12 to meet 45 minutes per Table 715.5.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, July 15, 2010 1:18 PM
To: [email protected]
Subject: RE: Small Orifice Sprinklers in Water Curtain

Is this stair supposed to be a protected exit?  Like normally in a rated shaft 
but now exposed due to glazing on one side?  So question is whether you're 
trying to emulate a certain fire resistance rating with these window sprinklers 
or just providing some sort of exposure protection?

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Thursday, July 15, 2010 3:36 PM
To: [email protected]
Subject: RE: Small Orifice Sprinklers in Water Curtain

The AHJ wants additional protection, to mitigate fire spread from the
interior toward exterior stairs in proximity to the affected openings.
The building code allows for protection of openings in a fully
sprinklered building by use of a water curtain per 903.3.1.1, i.e. NFPA
13.   We're going to cobble together the discharge criteria and
placement of a sprinkler over the interior side of each panel and call
it a day.  I don't write the copy, just reading the news into the
camera.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mike
Hairfield
Sent: Thursday, July 15, 2010 12:22 PM
To: AFSA SprinklerFORUM
Subject: RE: Small Orifice Sprinklers in Water Curtain


Shouldn't you be looking at Exposure Protection Sprinkler Systems which
allows different

K factors?

 

Mike
 
> Subject: Small Orifice Sprinklers in Water Curtain
> Date: Thu, 15 Jul 2010 12:12:11 -0700
> From: [email protected]
> To: [email protected]
> 
> Scenario: 3-story Light Hazard (Residential) occupancy,
> fully sprinklered per 13.
> 
> Situation: Exterior exit stairs are too close to glazed
> openings in exterior walls and 45-minute window protection is required
> (from inside out) for several 2'x3' fixed windows on all three floors.
> 
> Challenge: Can't use window sprinklers because exterior walls
> are bearing. Am proposing to use water curtain provisions of the
> building code, and furnish 3 GPM per lineal foot per 13.
> 
> 
> 
> Question: Since the windows are only 2' wide, and there are
> up to 3 windows in a cluster, we will have sprinklers at 4' apart in
> several areas and will be provided a baffle of some sort. I can
> easily hit my minimum flow rate with small orifice sprinklers and do
not
> see any restriction in 13 regarding orifice size in a water curtain.
> Since it's all Light Hazard, can anyone think of a reason why we can't
> use 4.2K pendents?
> 
> 
> 
> Steve Leyton
> 
> PROTECTION DESIGN & CONSULTING
> 
> 2851 Camino del Rio South, Suite 400
> 
> San Diego, CA 92108
> 
> -------------------------------------------------------------
> 
> Ph: 858.751.2930 - ext. 102
> 
> Fax: 858.751.2933
> 
> Cell: 619.972.5696
> 
> 
> 
> 
> 
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 5282 (20100715) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 5282 (20100715) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 5282 (20100715) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 5282 (20100715) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to