It is hard to visualize this to maintain reliability. Pond grass can be a
big problem. Then you need access to pump screens. I would not be in favor
of it do to reliability and maintenance.

Art  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Friday, July 16, 2010 10:56 AM
To: [email protected]
Subject: VT pump suction

I have a client that wants to use a vertical turbine pump taking suction out
of a pond. He wants to take suction directly from the pond without a
separate pit. I say he can suspend the pump into the pond, but he still has
to have an isolated sump with a trash rack for suction. Has anyone out there
done this before?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com