Sorry, didn't realize you had an over/under system, is it systems (2)? With
above and below (same piping you still would have to do the higher hazard)
and the light at 14.8 Q to prove which is more demanding. Make sense?  AS it
is an unrated wall and a fire could start on the sales side floor and go
into the storage area, right.

On Fri, Jul 16, 2010 at 5:59 PM, Hinson, Ryan <[email protected]> wrote:

> So are those heads above the ceiling over the sales area QR, and if so, are
> you using area reduction for that portion of the remain required remote
> area?
>
> Ryan Hinson
> Burns & McDonnell
> Direct: 952-656-6003 Ext 3662
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of ParsleyConsulting
> Sent: Friday, July 16, 2010 4:14 PM
> To: [email protected]
> Subject: Re: Adjacent hazards
>
> No, Tom, the remainder of the space is "light hazard" which is the space
> above the ceiling OVER the sales area.  The space under the ceiling is
> protected at 0.20 gpm/ft2, but the space at the combustible roof deck
> would only require LH density, even though the sprinklers there were
> spaced at 130 ft2 in the original install.
>
> Thanks,
> --
>
> PARSLEY CONSULTING
>
> Ken Wagoner, SET
>
> 760.745.6181 voice
>
> 760.745.0537 fax
>
> [email protected] <mailto:[email protected]> e-mail
>
> www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
>
>
>
>
> tom poisal wrote:
> > Ken thats how I see it. But the remainder of your space is "sales" which
> is
> > mercantile, ORD GP II - .2 density
> >
> > On Fri, Jul 16, 2010 at 2:24 PM, ParsleyConsulting <
> > [email protected]> wrote:
> >
> >
> >> Tom,
> >>
> >> I have a building which has a 260 sqft area which requires 0.5 gpm/sqft
> >> over 2,500 sqft due to storage commodity and height. The unrated walls
> >> separating the storage area from the sales area extend a foot above the
> >> 11'-0" ceiling in the sales area, while the storage area is open to the
> >> 16'-0" roof deck.  Total suite area is only 1,300 ft2.
> >>
> >> Do I have to extend the 0.5 density to the entire rest of the space
> >> above the ceiling which is adjacent and open to the storage room?  Or do
> >> I simply extend it 150'-0" past the room, based on Section and Table
> >> A.12.3 ('10 edition of -13)?
> >>
> >> My interpretation of those sections, along with 12.3(1) is that I'd have
> >> to provide 0.5 gpm/sqft over the storage area, plus 15'-0", while the
> >> remainder of the space would only require 0.10 gpm density for light
> >> hazard.  The high temp sprinklers would have to extend beyond the
> >> storage area by 30', but only the first 15' require the higher density.
> >>
> >> Does that line up with your thinking?
> >> --
> >>
> >> PARSLEY CONSULTING
> >>
> >> Ken Wagoner, SET
> >>
> >> 760.745.6181 voice
> >>
> >> 760.745.0537 fax
> >>
> >> [email protected] <mailto:[email protected]> e-mail
> >>
> >> www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
> >>
> >>
> >>
> >>
> >>
> >> tom poisal wrote:
> >>
> >>> Russell, the latter is correct, .3 over the area plus 15' border. the
> >>> balance is .2.  The size of the of the operating area is determined by
> >>>
> >> the
> >>
> >>> higher hazard. A.11.2.3.1.1 (02 handbook)
> >>>
> >>> On Fri, Jul 16, 2010 at 11:10 AM, Russell <[email protected]
> >>> wrote:
> >>>
> >>>
> >>>
> >>>> Please bear with me for not letting this topic go but I need to
> confirm
> >>>> something. I cannot remember the last time I dealt with adjacent
> hazards
> >>>> that were not separated by a partion.
> >>>> NFPA 13 '10 A11.1.2 leads me to believe that if a .3 density hazard
> >>>> requires 2500 s.f. then the remote area for that hazard would take in
> >>>>
> >> that
> >>
> >>>> area and as much of the .2 density hazard area as necessary to fulfill
> >>>>
> >> the
> >>
> >>>> 2500 s.f. (understanding that the .3 would not be required for the .2
> >>>>
> >> area).
> >>
> >>>> That doesn't seem just to me. If the .3 area plus the 15' border
> doesn't
> >>>> cover enough area to attain 2500 s.f. then use only all the area it
> does
> >>>> involve plus the border because the .2 occupany isn't the same fire
> >>>>
> >> threat.
> >>
> >>>> Does that make any sense?
> >>>>
> >>>> Russell
> >>>>
> >>>>
> >>>>
> >>>>
> >>>>
> >>>> ________________________________________________________________
> >>>> Sent via the WebMail system at brownautomatic.com
> >>>>
> >>>>
> >>>>
> >>>>
> >>>> _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> [email protected]
> >>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>>
> >>>> For Technical Assistance, send an email to: [email protected]
> >>>>
> >>>> To Unsubscribe, send an email
> >>>>
> >> to:[email protected]<to%[email protected]>
> <to%[email protected]<to%[email protected]>
> >
> >> <to%[email protected]<to%[email protected]>
> <to%[email protected]<to%[email protected]>
> >
> >>
> >>>> (Put the word unsubscribe in the subject field)
> >>>>
> >>>>
> >>>>
> >>>
> >>>
> >>>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> <to%[email protected]<to%[email protected]>
> >
> >> (Put the word unsubscribe in the subject field)
> >>
> >>
> >
> >
> >
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>



-- 
Tom Poisal, CET
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to