In the IBC, I-1 devolves to R-4 for 6 to 16 persons, AND further
devolves to R-3 or IRC for 5 or less. As seen in the I-1 occupancy
defined in Chapter 3.

On a related note, the 2009 IBC in Section 419 defines a new term:
live/work units.  The exception to R101.2 in the 2009 IRC Scope makes it
clear that when the live/work units are built to the IRC, they still
must use NFPA 13D, not the new IRC Section P2904 method.

 

David W. S. Blackwell, II, PE, CFI-I, CFPE
Engineering 
---------------------------------------------------------------- 
Office of State Fire Marshal 
141 Monticello Trail 
Columbia, SC 29203 
Phone:  803.896.9833 
Fax:  803.896.9806 
Email:  [email protected] 
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp 
---------------------------------------------------------------- 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Friday, August 13, 2010 1:43 PM
To: [email protected]
Subject: Re: Assisted Living Facility

This also could be classified as an I-1 which is generally more  
demanding than an R-4.  I mention this due to the exception in the IBC  
whereby an I-1 can be protected with 13D. IF teh building does not  
comply for an I-1, one could still discuss equivalencies in defining  
the type of system.

Roland

On Aug 13, 2010, at 8:17 AM, Jay White wrote:

> Good morning everyone, I have an assisted living facility with less  
> than 16
> persons. It was a large residential home turned into assisted  
> living. It is
> a group R-4 occupancy per IBC. Is the design based on NFPA 13? Could  
> design
> be based on NFPA 13D?
>
> Jay White
> Estimator/Design Manager
> Dynamic Fire Protection
> 1807 Hwy. 25 South
> Starkville, MS 39759
> Phone: 662-324-1550
> Fax:       662-324-1545
> Cell:      662-312-2426
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to