If you're in California (and some other states as well), amendments
require that all such systems be per 13.   Residential sprinkler
provisions still apply, but the design must be based on NFPA 13.


Steve Leyton
Protection Design & Consulting
 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Friday, August 13, 2010 11:26 AM
To: [email protected]
Subject: Re: Assisted Living Facility

Concur that is is required to be classified in the R category.  I was  
playing from memory and thought it was more optional verses a SHALL.

Back to the question on type of system.  I'm starting with the premise  
that 903.2.8 dictating protection per 903.3 allows any type of system  
that complies with the scope of the standard.  Since the scope of 13D  
is for one and two family dwellings and not residential occupancies,  
it does not cover assisted living facilities.

The point to be made is that a large I-1 can use a 13D (due to the IBC  
exception) so a smaller I-1 that has been assigned a less demanding  
occupancy classification is quacking like the same duck regarding  
needed level of protection.  Since it is not stated that way in the  
IBC, one has to discuss equivalencies with the AHJ.

Roland

On Aug 13, 2010, at 10:55 AM, David Blackwell wrote:

> In the IBC, I-1 devolves to R-4 for 6 to 16 persons, AND further
> devolves to R-3 or IRC for 5 or less. As seen in the I-1 occupancy
> defined in Chapter 3.
>
> On a related note, the 2009 IBC in Section 419 defines a new term:
> live/work units.  The exception to R101.2 in the 2009 IRC Scope  
> makes it
> clear that when the live/work units are built to the IRC, they still
> must use NFPA 13D, not the new IRC Section P2904 method.
>
>
>
> David W. S. Blackwell, II, PE, CFI-I, CFPE
> Engineering

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 5365 (20100813) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 5365 (20100813) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to