This also could be classified as an I-1 which is generally more demanding than an R-4. I mention this due to the exception in the IBC whereby an I-1 can be protected with 13D. IF teh building does not comply for an I-1, one could still discuss equivalencies in defining the type of system.

Roland

On Aug 13, 2010, at 8:17 AM, Jay White wrote:

Good morning everyone, I have an assisted living facility with less than 16 persons. It was a large residential home turned into assisted living. It is a group R-4 occupancy per IBC. Is the design based on NFPA 13? Could design
be based on NFPA 13D?