Todd,

I think in the end what this all boils down to is the owner hires the
contractor to do the work. If it's a job that could be acceptable,
like this, you say OK, apply for a permit stating your intention, and
then wait for approval. If you think the AHJ is a moron and that maybe
this is something that ought not be approved you be very specific and
give the AHJ hints so that he may find his own way through the morass
of coes and regulations (similar to what you'd do when he comes up
with an "A-code, something he just pulls out of his ....). If the
owner wants you to do something you know won't fly or is just bad
practice (like turning it into a dry system by turning off the water
or putting a double interlock pre-action system in a computer room)
you state your objections and reasons to him, apply for the permit if
he still wants to do it, and wait for approval. Again, if the AHJ is a
moron.... Bottom line is we aren't the fire police. As contractors we
aren't even code consultants but are only responsible for installing
the system per the rules of installation. When we open our mouths
about codes and start offering advice or design the system (in the
sense of making design,not merely layout decisions) then we cross the
line into the world of the design professional. Now the reality, as we
all know, is that you can't not cross that line almost always so your
advice and handling of the decisions had better be well informed.

On Sat, Aug 14, 2010 at 5:46 AM, Todd Williams <[email protected]> wrote:
> Here is another interesting point. If the fire marshal had previously
> approved this for use as storage without having the system evaluated, does
> this now fall under an existing condition and no longer considered a change
> of use?
>
>
>
> At 12:45 AM 8/12/2010, you wrote:
>>
>> Matt,
>>
>> 25 would not be the driver, nor would 13. It's the building codes. And
>> I wouldn't necessarily call Art's scenario an "occupancy" change. It
>> might be or it might not depending on definitions in the building
>> code. Another driver would be the owner if he wanted to assess whether
>> an upgrade would be a good idea or not. The owner can do what he wants
>> within the code. The code enforcement officer can require whatever the
>> code authorizes him to do. The contractor or other hired hand
>> (engineer) can make recommendations but drives no decision.
>>
>> On Wed, Aug 11, 2010 at 9:31 PM, [email protected]
>> <[email protected]> wrote:
>> > Art, what you are stating is an occupancy change. (introducing a high
>> > hazard) as opposed to just going from wet to dry. That WOULD require calcs.
>> > Changing a system to dry for the same occupancy does not. Should it? Yes, 
>> > in
>> > my opinion, but not per 25 .
>> >
>> > My HTC EVO 4 made cobbler out of your Blackberry!!
>> >
>> > ----- Reply message -----
>> > From: "Art Tiroly" <[email protected]>
>> > Date: Wed, Aug 11, 2010 4:11 pm
>> > Subject: pipe schedule and storage
>> > To: "[email protected]"
>> > <[email protected]>
>> >
>> > I have a real problem with this concept. This sounds like a system with
>> > 3/4"
>> > end lines that was meant for manufacturing. If you intruduce a high
>> > hazard
>> > process or storage that will not be controlled by this old schedule
>> > system,
>> > it is till OK to not require that sprinkler system be calculated to the
>> > requirements of the new occupancy?
>> >
>> > If it is a calculated OH2 system does that need to be brought up to the
>> > requirements of the hazard due to the change in occupancy?
>> >
>> > Art Tiroly/AFSA
>> > ATCO Fire Protection
>> >
>> > -----Original Message-----
>> > From: [email protected]
>> > [mailto:[email protected]] On Behalf Of Ron
>> > Greenman
>> > Sent: Wednesday, August 11, 2010 4:15 PM
>> > To: [email protected]
>> > Subject: Re: pipe schedule and storage
>> >
>> > Again, I don't know why it would need to even comply with chapter 22
>> > unless
>> > there is something in the applicable building code with any legal
>> > amendments
>> > or in a local ordinance that would drive an upgrade to current code.
>> > When I
>> > worked for a building department in California we had if the occupancy
>> > changed or if the new work exceeded 25% of the assessed value of the
>> > building for drivers. Other than that only NEW work needed to meet the
>> > current code and then was modified by language such as Forest cites
>> > about
>> > new work to old pipe schedule systems needing to maintain the pipe
>> > schedule..
>> > Whatever your current 13 is it is the standard for INSTALLATION of
>> > sprinkler
>> > systems, not the revamping of existing systems. That is still governed
>> > by
>> > version of 13 under which the system was installed unless some other
>> > piece
>> > of legislation contravenes or the existing condition is a danger to
>> > public
>> > health or safety.
>> >
>> > On Wed, Aug 11, 2010 at 12:54 PM, Forest Wilson
>> > <[email protected]>
>> > wrote:
>> >> Roland is correct.
>> >> NFPA does not state a 30% increase requirement.
>> >> NFPA 13-11.2.3.2.5 requires a 30% increase for hydraulically
>> >> calculated systems.
>> >> However, 13-11.2.2.3 clearly states that "Additions or modifications
>> >> to existing pipe schedule systems sized according to the pipe
>> >> schedules"..shall be permitted.
>> >> So, provided that the system piping complied with Chapter 22,this
>> >> system could be converted from wet to dry using the pipe schedule
>> >> system. It could be considered a modification not requiring hydraulic
>> >> calcs with the increase.
>> >>
>> >> Forest Wilson
>> >> Cherokee Fire
>> >>
>> >> -----Original Message-----
>> >> From: [email protected]
>> >> [mailto:[email protected]] On Behalf Of John
>> >> O'Connor
>> >> Sent: Wednesday, August 11, 2010 12:34 PM
>> >> To: [email protected]; [email protected]
>> >> Subject: RE: pipe schedule and storage
>> >>
>> >> And if the system is converted to dry can the existing pipe schedule
>> >> afford the 30% area increase while flowing water thru two pieces of 1"
>> >> at the end of all lines.  I doubt it.
>> >> John O'Connor
>> >>
>> >> -----Original Message-----
>> >> From: [email protected]
>> >> [mailto:[email protected]] On Behalf Of Brad
>> >> Sent: Wednesday, August 11, 2010 11:26 AM
>> >> To: [email protected]
>> >> Subject: RE: pipe schedule and storage
>> >>
>> >> And hopefully it was installed long enough ago that sloping the pipe
>> >> to drain was required on wet systems too
>> >>
>> >> -----Original Message-----
>> >> From: [email protected] [mailto:[email protected]]
>> >> Sent: Wednesday, August 11, 2010 11:21 AM
>> >> To: [email protected]
>> >> Subject: RE: pipe schedule and storage
>> >>
>> >> Typically if you're not touching the old system it can stay in place
>> > as-is.
>> >> BUT if they want to modify it and try to change from wet to dry (good
>> >> luck with that) then it's game over and it has to meet current codes.
>> >> The whole idea of grandfathering in non-compliant systems is a
>> >> misnomer.
>> >>
>> >> Plus the big thing, how can you prove the system will function when
>> >> changing from wet to dry without calculating it?
>> >>
>> >> Besides, when did the owner become a code and fire protection expert?
>> >> You just gotta love it.
>> >>
>> >> Craig L. Prahl, CET
>> >> Fire Protection Specialist
>> >> Mechanical Department
>> >> CH2MHILL
>> >> Lockwood Greene
>> >> 1500 International Drive
>> >> Spartanburg, SC  29304-0491
>> >> Direct - 864.599.4102
>> >> Fax - 864.599.8439
>> >> [email protected]
>> >> http://www.ch2m.com
>> >>
>> >>
>> >> -----Original Message-----
>> >> From: [email protected]
>> >> [mailto:[email protected]] On Behalf Of Todd
>> >> Williams
>> >> Sent: Wednesday, August 11, 2010 12:14 PM
>> >> To: [email protected]
>> >> Subject: pipe schedule and storage
>> >>
>> >> I think I have this one, but could use a little more ammo. I walked
>> >> through an old mill building this morning with an old OH pipe schedule
>> >> system. (They want to convert from wet to dry). In the building, they
>> >> have some 8 ft storage of a Group A plastics in cardboard cartons and
>> >> well as 2 piles of idle pallets to 8 ft. The owner is claiming that
>> >> the pipe schedule is grandfathered and the system does not need to
>> >> meet the hydraulic criteria. I disagree and am basing most of my
>> >> argument on the water supply requirements in
>> >> 11.2.2 (NFPA 13, 2002 edition). Any other thoughts?
>> >>
>> >> Todd G. Williams, PE
>> >> Fire Protection Design/Consulting
>> >> Stonington, CT
>> >> 860.535.2080
>> >> www.fpdc.com
>> >>
>> >> _______________________________________________
>> >> Sprinklerforum mailing list
>> >> [email protected]
>> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >>
>> >> For Technical Assistance, send an email to: [email protected]
>> >>
>> >> To Unsubscribe, send an email
>> >> to:[email protected]
>> >> (Put the word unsubscribe in the subject field)
>> >> _______________________________________________
>> >> Sprinklerforum mailing list
>> >> [email protected]
>> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >>
>> >> For Technical Assistance, send an email to: [email protected]
>> >>
>> >> To Unsubscribe, send an email
>> >> to:[email protected]
>> >> (Put the word unsubscribe in the subject field)
>> >>
>> >> _______________________________________________
>> >> Sprinklerforum mailing list
>> >> [email protected]
>> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >>
>> >> For Technical Assistance, send an email to: [email protected]
>> >>
>> >> To Unsubscribe, send an email
>> >> to:[email protected]
>> >> (Put the word unsubscribe in the subject field)
>> >>
>> >> No virus found in this incoming message.
>> >> Checked by AVG - www.avg.com
>> >> Version: 9.0.851 / Virus Database: 271.1.1/3064 - Release Date:
>> >> 08/11/10 01:34:00
>> >>
>> >> _______________________________________________
>> >> Sprinklerforum mailing list
>> >> [email protected]
>> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >>
>> >> For Technical Assistance, send an email to: [email protected]
>> >>
>> >> To Unsubscribe, send an email
>> >> to:[email protected]
>> >> (Put the word unsubscribe in the subject field)
>> >>
>> >> _______________________________________________
>> >> Sprinklerforum mailing list
>> >> [email protected]
>> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >>
>> >> For Technical Assistance, send an email to: [email protected]
>> >>
>> >> To Unsubscribe, send an email
>> >> to:[email protected]
>> >> (Put the word unsubscribe in the subject field)
>> >>
>> >
>> >
>> >
>> > --
>> > Ron Greenman
>> > Instructor
>> > Fire Protection Engineering
>> > Bates Technical College
>> > 1101 So. Yakima Ave.
>> > Tacoma, WA
>> >
>> > 253.680.7346
>> >
>> > Member:
>> > AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
>> >
>> > They are happy men whose natures sort with their vocations. -Francis
>> > Bacon,
>> > essayist, philosopher, and statesman (1561-1626)
>> > _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> > For Technical Assistance, send an email to: [email protected]
>> >
>> > To Unsubscribe, send an email
>> > to:[email protected]
>> > (Put the word unsubscribe in the subject field)
>> >
>> > _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> > For Technical Assistance, send an email to: [email protected]
>> >
>> > To Unsubscribe, send an email
>> > to:[email protected]
>> > (Put the word unsubscribe in the subject field)
>> > _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> > For Technical Assistance, send an email to: [email protected]
>> >
>> > To Unsubscribe, send an email
>> > to:[email protected]
>> > (Put the word unsubscribe in the subject field)
>>
>>
>>
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering
>> Bates Technical College
>> 1101 So. Yakima Ave.
>> Tacoma, WA
>>
>> 253.680.7346
>>
>> Member:
>> AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, NIBS, WSAFM, WFC
>>
>> They are happy men whose natures sort with their vocations. -Francis
>> Bacon, essayist, philosopher, and statesman (1561-1626)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA

253.680.7346

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to