This will not stop bothering me because it is absolutely backwards. Is there
any doubt that requiring standard response on Dry and PA only aggravates an
inherent delay? (now I can let UFC-600-01 go and think about NFPA 13)
NFPA 13, after '96, requires QR for light haz. Would there be any value in
terms of better FP if 13 also required QR for DRY and PA ORD1 and 2? 


-----Original Message-----
From: Brad [mailto:[email protected]] 
Sent: Friday, August 20, 2010 10:07 AM
To: 'Ron Greenman'; [email protected]
Subject: RE: UFC 3-600-01 interpretation

Robust is good. The increased areas and hose demands are fine (treating all
occupancies as HPRs). I found Change 1, 14 July 2009 (to UFC 3-600-01, 26
September 2006)- it resolved my 'similar situation' comment, ~sch 40
galvanized in and out, all sizes, for Dry and PA, no exceptions~, long
lasting is good. But QR limited to wet pipe systems has not changed, and I
am still wondering what the reasoning for that is.

-----Original Message-----
From: Ron Greenman [mailto:[email protected]] 
Sent: Thursday, August 19, 2010 7:40 PM
To: [email protected]; [email protected]
Subject: Re: UFC 3-600-01 interpretation

Not directed at anyone in particular but offered merely as observation:

Having been asked for an opinion on more than one occasion by one or
more of the Navy guys having input on the original Unified Facilities
Criterion I can pretty much assure you that there is no oversight.
Every deviation from NFPA or FM that was suggested was well vetted
before a decision was made and the fact is that the military wants
stuff that works everywhere it's likely to be and they want it
durable, robust and long lasting. Small arms have to work in sub-artic
climates and in the desert. They have to work reliably for long
periods with minimal maintenance. Field maintenance has to be simple
even if you're in the dark, wearing gloves, under stress,
simple-minded, and any other deterrent to calm and casual weapons
maintenance. I'd venture that tis philosophy transfers to fire
protection. Unfortunately when funds are low fire protection IT&M
suffers so that robust and reliable at construction time is even more
important.

On Thu, Aug 19, 2010 at 12:53 PM, Brad <[email protected]> wrote:
> That is what I was afraid of and now I am disturbed by things like 'can of
> worms', and 'swept under the rug'. It is fine if the reviewer uses logic
and
> reason to get from one thing to another (this is America). A similar
> situation is the use of schedule 10/40 vs water corrosiveness-- then ~sch
40
> for Dry and PA, no exceptions~, without saying except galvanized.
>
> -----Original Message-----
> From: Thom [mailto:[email protected]]
> Sent: Thursday, August 19, 2010 2:22 PM
> To: [email protected]; [email protected]
> Subject: RE: UFC 3-600-01 interpretation
>
> No! but I guarantee that you can get one (a different one) from every
CORP,
> NAVFAC or Air Force gov. FPE.
>
> Thom
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Brad
> Sent: Thursday, August 19, 2010 11:04 AM
> To: [email protected]
> Subject: UFC 3-600-01 interpretation
>
> From UFC 3-600-01, 26 September 2006, 4-2.3.4:
>
> 'The use of quick response automatic sprinklers (QRAS) is limited to wet
> pipe systems'.
>
> This is following the allowance of "QR Reduction" when as per NFPA 13.
>
> I think the intent of 4-2.3.4 is '. the use of QR Reduction is limited to
> wet .', otherwise there could be trouble with dry, Light Haz, Corp jobs,
> right? Is there such a thing as UFC Formal Interpretations?
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA

253.680.7346

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to