Where does it say that no protection is needed if the siding has a flame spread 
of 25 or less?
 
Is this situation related to a requirement for protection under a canopy of 
combustible construction, or if there is combustible storage under the canopy?  
 
Generically speaking, vinyl (PVC) when heated releases chlorine compounds that 
inhibit combustion.  This is why rigid PVC is treated as a Group C plastic, 
rather than Group A, like most plastics we deal with.  But when exposed to an 
adjacent fire, vinyl siding will burn and fire will go right up to the canopy 
or soffit.  If there are soffit vents that lead to a wood frame attic, you can 
have a disastrous fire.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 
2715 Harrison St. 
Evanston, IL 60201 
Tel: 847-733-0944 
Fax: 847-866-6255 



--- On Tue, 9/7/10, Greg McGahan <[email protected]> wrote:


From: Greg McGahan <[email protected]>
Subject: vinyl soffits
To: [email protected]
Date: Tuesday, September 7, 2010, 8:15 PM


In the past we have installed systems for vinyl storage and been met with very 
mixed assessments of the criteria it should fall under by members of this forum 
and various Engineers of Record. Recently we posed an RFI to an Arch and Eng 
design team that stated that at least one vinyl siding product had a flame 
spread of 25 or less and therefore would not create a need for protection under 
an exterior canopy. I have never heard this before now.

So the question is that if there is an exterior walkway covered with typical 
everyday plain old vinyl siding at the ceiling: would sprinklers be required if 
this were the only questionable component?

There are a myriad of existing such situations in which we happen to find 
ourselves at the present time and determining the manufacturer and exact 
material would be virtually impossible.

Thanks for the help as always!
-- _______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to