To my knowledge there isn't a code or standards based restriction on
using this tube for a dry standpipe - I'm assuming the FDC?   We have
done it on a few projects and haven't heard of any problems in the
field.   The one thing to remember is that water pressure causes the
gasket seals to swell in the bell ends, so if there's a problem with dry
pipe application it likely would be found there.   The thrust
restraints, bury depths, etc. should all be undertaken for the maximum
anticipated pressure, i.e. whatever the FD tells you they're going to
pump.   


Steve Leyton
Protection Design & Consulting
 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Charles
Thurston
Sent: Tuesday, September 07, 2010 2:51 PM
To: sprinklerforum
Subject: Manual Dry standpipe

Hello sprinklerforum,

  I can not find anyplace where C900 pipe is not allowed for the
underground portion of a manual dry standpipe. Am I missing it somewhere
?

-- 
Best regards,
 Charles Thurston                          mailto:[email protected]
  Coastal Fire Protection/ Myrtle Beach Fire & Safety Group.
  AFAA Guest

Electronic Privacy Notice:
This e-mail, and any attachments, contains information that is, or may  
be, covered by electronic communications privacy laws, and is also  
confidential and proprietary in nature. If you are not the intended  
recipient, please be advised that you are legally prohibited from  
retaining, using, copying, distributing, or otherwise disclosing this  
information in any manner. Instead, please reply to the sender that  
you have received this communication in error, and then immediately  
delete it. Thank you in advance for your cooperation

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to