Sounds like the AHJ may be overstepping his boundries. Additions to Pipe schedule systems are allowed without calcs in #13.
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of steve Sent: Thursday, September 16, 2010 10:10 AM To: AFSA Subject: Re: Pipe Schedule Systems The standard requires a minimum pressure be available at the highest/most remote sprinkler - is that the "calc" that's been requested? Still no requirement for a hose allowance though. Steve Sent from my Verizon Wireless BlackBerry -----Original Message----- From: "Matthew J. Willis" <[email protected]> Sender: [email protected] Date: Thu, 16 Sep 2010 08:59:48 To: <[email protected]> Reply-To: [email protected] Subject: RE: Pipe Schedule Systems Then it will no longer be a pipe schedule, but a calculated system. Which requires hose streams. R/ Matt Matthew J. Willis, CET Automatic Fire Sprinklers Norred Fire Systems L.L.C. 318-387-1134 Voice 318-816-1087 Mobile 318-387-1163 Facsimile [email protected] > >-----Original Message----- > >From: [email protected] > >[mailto:sprinklerforum- [email protected]] On Behalf Of Brian > >Harris > >Sent: Thursday, September 16, 2010 8:57 AM > >To: [email protected] > >Subject: RE: Pipe Schedule Systems > > > >David- > >We are doing some minor work to an existing warehouse that was done > >with the pipe schedule method. Now the AHJ wants us to provide > >hydraulic calc's to show him if the existing system will work. > > > >Brian Harris > >FDFP Inc. > > > >-----Original Message----- > >From: [email protected] > >[mailto:[email protected]] On Behalf Of Autry, > >David > >Sent: Thursday, September 16, 2010 9:39 AM > >To: [email protected] > >Subject: RE: Pipe Schedule Systems > > > >What exactly would you add it to? > > > >David Autry > >Plans Examiner > >Nebraska State Fire Marshal's Office > >246 S. 14th Street > >Lincoln, NE 68508 > >402-471-9659 > >402-471-3118 fax > >www.sfm.ne.gov > > > >** Note new email address: [email protected] > > > >-----Original Message----- > >From: [email protected] > >[mailto:[email protected]] On Behalf Of Brian > >Harris > >Sent: Thursday, September 16, 2010 8:36 AM > >To: [email protected] > >Subject: Pipe Schedule Systems > > > >I swear I read somewhere that for a pipe schedule system you do not > >need to add hose allowance, Am I nuts? > > > > > > > >Brian Harris > > > >First Defense Fire Protection > > > >11957 Ramah Church Road > > > >Huntersville, NC 28078 > > > >Phone: 704.948.3506 > > > >Fax: 704.948.3507 > > > >Nicet # 128476 > > > > > > > > > > > > > > > >======= > >Email scanned by PC Tools - No viruses or spyware found. > >(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890) > >http://www.pctools.com/ ======= > >_______________________________________________ > >Sprinklerforum mailing list > >[email protected] > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > >For Technical Assistance, send an email to: [email protected] > > > >To Unsubscribe, send an email > >to:[email protected] > >(Put the word unsubscribe in the subject field) > >_______________________________________________ > >Sprinklerforum mailing list > >[email protected] > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > >For Technical Assistance, send an email to: [email protected] > > > >To Unsubscribe, send an email > >to:[email protected] > >(Put the word unsubscribe in the subject field) > > > > > > > > > > > >======= > >Email scanned by PC Tools - No viruses or spyware found. > >(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890) > >http://www.pctools.com/ ======= > > > > > > > > > > > >======= > >Email scanned by PC Tools - No viruses or spyware found. > >(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890) > >http://www.pctools.com/ ======= > >_______________________________________________ > >Sprinklerforum mailing list > >[email protected] > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > >For Technical Assistance, send an email to: [email protected] > > > >To Unsubscribe, send an email > >to:[email protected] > >(Put the word unsubscribe in the subject field) No virus found in > >this incoming message. > >Checked by AVG - www.avg.com > >Version: 9.0.851 / Virus Database: 271.1.1/3137 - Release Date: > >09/16/10 > >01:34:00 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)